Sending numeric data
This procedure sets up communication with Digital Outputs using through a Group Output. This is a simple way to transmit numeric data to another device in the field. Group Output 1 will be set as a 16-bit word. DO[33] to DO[48] will be used to transmit the data. Digital Outputs must be configured as usual. This procedure is typical for Omron NX I/O block.
+/- 5 minutes
Make sure to create a backup of your settings before making any modifications.
If your Inputs/Outputs aren’t set properly, a mechanical system could be activated by inadvertence.
- PRESS –> [ I/O ]
- PRESS –> [ F1 ] [ TYPE ]
- SELECT –> [ 5 ] 5 GROUP (see screenshot)
- PRESS –> [ IN/OUT ] (If you don’t have the screen of “I/O Group Out”)
- PRESS –> [ F2 ] CONFIG
- Using Arrow on line of GO #1, ENTER –> 89 in “RACK” column. (Corresponding to Ethernet I/P rack number)
- Using Arrow on line of GO #1, ENTER –> 1 in “SLOT” column. (Corresponding Slot of Ethernet I/P set up for this particular device)
- Using Arrow on line of GO #1, ENTER –> 33 in “START PT” column. (Corresponding Start bit of Ethernet I/P set up for Digital outputs)
- Using Arrow on line of GO #1, ENTER –> 16 in “NUM PTS” column. (Corresponding to the number of bits composing the numeric data. In this case, it is a 16 bits word)
- PRESS –> [ ENTER ] (see screenshot)
- PRESS –> [ FCTN ]
- SELECT –> [ 8 ] 8 CYCLE POWER (see screenshot)
- PRESS –> [ YES ] (see screenshot)
To check if this procedure works, put in a program something like this line: GO[1]= 65535. Run this line in STEP mode. All Digital Outputs from DO[33] to DO[48] will be ON. (see screenshot)